    New Insteon 2441TH does not boot / power on

    I replaced an existing automatic thermostat with a new 2441TH Insteon thermostat today. The previous thermostat was wired with a 5 wire cable. I carefully moved the wires to the new Insteon device. The screen on the Insteon never powers up (remains blank) and no LEDs are lit. Maybe this is a defective unit?

    I took a picture of the completed wiring (attached)

    Thanks in advance
    You do not have permission to view this gallery.
    This gallery has 1 photos.

    #2
    Was the old thermostat powered by the heating equipment?
    You may want to look at the control end of the cable and verify the Blue COM wire is connected to the controls common.
    If you have an AC volt meter. It should be around 24VAC from COM to 24RH

    Comment


      #3
      Indeed, while I had all 5 wires at the thermostat end, the red and blue wires were not properly connected on the air handler end.
      thanks!

      Comment


        #4
        Good to see it was a easy fix and the thermostat was not bad.